معمای ترانسفورماتور شماره 24- موازی نمودن ترانسفورماتورهای تکفاز
آیا میتوان دو ترانسفورماتور تکفاز که غیر مشابه هستند را موازی بست!؟
نویسنده : کیان - از: رشت
 
#1
ساعت: 10:51 - تاریخ: 8 آبان 1389
بطور کلی خیر، البته برخی رواداریها برای انحرافات مختصر در استانداردها پیش بینی شده است که در زیر به برخی از آنها اشاره شده است.

The satisfactory parallel operation of transformers is dependent upon five principal characteristics; that is, any two or more transformers which it is desired to operate in parallel should possess:
1. The same inherent phase angle difference between primary and secondary terminals.
2. The same voltage ratio.
3. The same percentage impedance.
4. The same polarity.
5. The same phase sequence.

To a much smaller extent parallel operation is affected by the relative outputs of the transformers, but actually this aspect is reflected into the third characteristic since, if the disparity in outputs of any two transformers exceeds three to one it may be difficult to incorporate sufficient impedance in the smaller transformer to produce the correct loading conditions for each unit.
Characteristics 1 and 5 only apply to polyphase transformers. A very small degree of latitude may be allowed with regard to the second characteristic mentioned above, while a somewhat greater tolerance may be allowed with the third, but the polarity and phase sequence, where applicable, of all transformers operating in parallel must be the same.
Generally three phase transformers are in parallel operation if they are connected in parallel on at least two sides. A distinction is made between busbar interconnection and network interconnection. The following conditions must be satisfied in order to avoid dangerous
transient currents:
1. Vector groups should have the same phase angle number; terminals of the same designation must be connected together on the HV and LV sides; Exception: Phase angle numbers 5 and 11 (Table below);
2. The ratios should be as similar as possible, i.e. the same rated voltages on the HV and LV sides;
3. Approximately the same impedance voltages uk maximum permissible discrepancies ± 10 %. In the event of larger differences, an inductance (reactor) can be connected ahead of the transformer with the lower impedance voltage.
4. Rated output ratio smaller than 3:1.



The theory of the parallel operation of single-phase transformers is essentially the same as for three-phase, but the actual practice for obtaining suitable connections between any two single-phase transformers is considerably simpler than the determination of the correct connections for any two three-phase transformers.
In single-phase transformers phase angle difference between primary and secondary terminals does not arise, as by the proper selection of external leads any two single-phase transformers can be connected so that the phase angle difference between primary and secondary terminals is the same for each. Consequently the question really becomes one of polarity.

It is very desirable that the voltage ratios of any two or more transformers operating in parallel should be the same, for if there is any difference whatever a circulating current will flow in the secondary windings of the transformers when they are connected in parallel, and even before they are connected to any external load. Such a circulating current may or may not be permissible.
This is dependent firstly on its actual magnitude and, secondly, on whether the load to be supplied is less than or equal to the sum of the rated outputs of the transformers operating in parallel. As a rule, however, every effort should be made to obtain identical ratios, and particular attention should be given to obtaining these at all ratios when transformers are fitted with tappings.
In passing, it may be well to point out that when a manufacturer is asked to design a transformer to operate in parallel with existing transformers, the actual ratio of primary and secondary turns should be given, as this ratio can easily be obtained exactly. Such figures would, of course, be obtained from the works test certificate for the existing transformers.
It is to be noted that this flow of circulating current takes place before the transformers are connected up to any external load. A circulating current in the transformer windings of the order of, say, 5% of the full-load current may generally be allowed in the case of modern transformers without any fear of serious overheating occurring. It is sometimes very difficult to design new transformers to give a turns ratio on, say, four tappings identical to what an existing one may possess, and while it is desirable that the ratios should be the same, it is not necessary to insist on their being identical.
 
نویسنده : حمید - از: فیروزآباد فارس
 
#2
ساعت: 10:45 - تاریخ: 10 اسفند 1390
یک عدد اختلاف در گروه برداری باعث عبور 4.7 جریان نامی گردشی بین دو ترانس موازی می گردد به عبارتی سبب سوختن ترانس ها می شود  
نویسنده : تقوی - از: کازرون
 
#3
ساعت: 11:53 - تاریخ: 10 اسفند 1390
ببخشید من  ترانس سه فاز  مد نظرم بود. 
نویسنده : تقوی - از: کازرون
 
#4
ساعت: 15:33 - تاریخ: 10 اسفند 1390
لطفاً مبنا یا منبع فرمایشتان را ذکر فرمائید. 
نویسنده : مدیر سایت
 
#5
ساعت: 00:06 - تاریخ: 29 شهریور 1393
برای موازی کردن ترانس تکفاز چند نکته مهم هستند از قبیل درصد ولتاژ اتصال کوتاه، توان، ولتاژ خروجی که ترانس با درصداتصال کوتاه کمتر متحمل فشار بار بیشتر میشود. 