معمای ترانسفورماتور شماره 96 - ترانس ایزوله
علت استفاده از ترانسفورماتورهای ایزوله یک به یک  در تغذیه سیستم های  DCS و ESD  چیست؟
نویسنده : علی - از: ایران
 
#1
ساعت: 17:12 - تاریخ: 23 آذر 1392
ترانسهای ایزوله در مدارات الکترونیک با هدف حذف بخشی از هارمونیکهای مزاحم، تأمین نول مجازی و بی خطر، تأمین فیلترینگ در قبال سیگنالهای فرکانس بالا به دلیل امپدانس ذاتی ترانس و ایزولاسیون الکترواستاتیک بکار می روند.

Shielded isolation transformer
A shielded transformer is a two-winding transformer, usually delta–star connected and serves the following purposes:
Voltage transformation from the distribution voltage to the equipment’s utilization voltage.
Converting a 3-wire input power to a 4-wire output thereby deriving a separate stable neutral for the power supply wiring going to sensitive equipment.
Keeping third and its multiple harmonics away from sensitive equipment by allowing their free circulation in the delta winding.
Softening of high-frequency noise from the input side by the natural inductance of the transformer, particularly true for higher frequency of noise for which the reactance becomes more as the frequency increases.
Providing an electrostatic shield between the primary and the secondary windings thus avoiding transfer of surge/impulse voltages passing through inter-winding capacitance.
Figure 8.27 shows the principle involved in a shielded transformer. The construction of the transformer is such that the magnetic core forms the innermost layer, followed by the secondary winding, the electrostatic shield made of a conducting material (usually copper) and finally the primary winding. Figure 8.28 shows this detail. It can be seen that the high-frequency surge is conducted to ground through the capacitance between the primary winding (on the left) and the shield, which is connected to ground. Besides the shield, the magnetic core, the neutral of the secondary winding and the grounding wire from the electronic equipment are all terminated to a ground bar, which in turn, is connected to the power supply ground/building ground. It is also important that the primary wiring to and secondary wiring from the isolation transformer are routed through separate trays/conduits. If this is not done, the inter-cable capacitances may come into play negating the very purpose of the transformer.


 
نویسنده : حمید - از: فیروزآباد فارس
 