معمای ترانسفورماتور شماره 86 - بانک کردن دو ترانس
در بعضی از ایستگاههای فشار قوی در ایران برای افزایش ظرفیت ترانس های ایستگاه، یک ترانس جدید را با یکی از ترانس های موجود و با حفاظت مشترک بانک میکنند (بدون احداث بی جدید) آیا این موضوع استاندارد است - لطفا توضیح دهید.
نویسنده : سپهر - از: ایران- فارس
 
#1
ساعت: 11:06 - تاریخ: 23 خرداد 1392
موازی کردن دوترانس هم سایز از نقطه نظر حفاظتی هر گاه متکی به یک سیستم حفاظتی باشیم ، نیازمند ملاحظاتی است که در کتاب هنر رله گذاری بدان پرداخته شده است.

From the standpoint of protective relaying, the operation of two transformer banks in parallel without individual breakers is to be avoided. In order to obtain protection equivalent to that when individual breakers are used, the connections of Figure below would be required. To protect two equally rated banks as a unit, using only CT's on the source sides of the common breakers and a single relay is only half as sensitive as protecting each bank from its own CT's; this is because the CT ratios must be twice as high as if individual CT's were used for each bank, both banks being assumed to have the same rating, and as a result the secondary current for a given fault will be only half as high. If one bank is smaller than the other, its protection will be less than half as sensitive. With more than two banks, the protection is still poorer.



When parallel transformer banks having individual breakers are located some distance away from any generating station, a possibly troublesome magnetizing-current-inrush problem may arise. If one bank is already energized and a second bank is then energized, magnetizing-current inrush will occur-not only to the bank being energized but also to the bank that is already energized. Moreover, the inrush current to both banks will decay at a much slower rate than when a single bank is energized with no other banks in parallel.
The magnitude of the inrush to the bank already connected will not be as high as that to the bank being switched, but it can easily exceed twice the full-load-current rating of the bank; the presence of load on the bank will slightly reduce its inrush and increase its rate of decay.
Briefly, the cause of the foregoing is as follows: The d-c component of the inrush current to the bank being energized flows through the resistance of transmission-line circuits between the transformer banks and the source of generation, thereby producing a d-c voltage-drop component in the voltage applied to the banks. This d-c component of voltage causes a build-up of d-c magnetizing current in the already-connected bank, the rate of which is the same as the rate at which the d-c component of magnetizing current is decreasing in the bank just energized. When the magnitudes of the d-c components in both banks become equal, there is no dc component in the transmission-line circuit feeding the banks, but there is a d-c component circulating in the loop circuit between the banks. The time constant of this trapped d--c circulating current, depending only on the constants of the loop circuit, is much longer than the time constant of the d-c component in the transmission-line circuit feeding the banks. Figure above shows the circuits involved and the magnetizing-current components in each circuit.
The significance of the foregoing is two-fold. First, desensitizing means already described for preventing differential-relay operation on magnetizing-current inrush are not effectivein the bank that is already energized. Only time delay in the operation of the differential relay will be elective in preventing undesired tripping. However, if the banks are protected by separate relays having tripping suppression or harmonic restraint, no undesired tripping will occur. Second, if the banks are protected as a unit, even the harmonic-current restraint type may cause undesired tripping because, as shown in Fig. , the total-current wave very shortly becomes symmetrical and does not contain the necessary even harmonics required for restraint.
 
نویسنده : حمید - از: فیروزآباد فارس
 