Protection riddle No.74 - REF Protection on 2MVA Transformer
Advantages  of providing REF protection on 2MVA,22KV/433v Dyn11 Transformer,Having Z% 6.25.What should be ideal CT specs on transformer neutral and in LT panel.
Author : Manish Naha - From: S N Joshiconsultants,Pune, India
 
#1
Thu, July 22nd, 2010 - 19:02
REF as one of important unit protection can be applied throughout a power transformer and, since it does not involve time grading, is relatively fast in operation. The speed of response is substantially independent of fault severity.
Unit protection usually involves comparison of quantities at the boundaries of the protected zone as defined by the locations of the current transformers. This comparison may be achieved by direct hard-wired connections or may be achieved via a communications link. However certain protection systems derive their 'restricted' property from the configuration of the power system and may be classed as unit protection, e.g. earth fault protection applied to the high voltage delta winding of a power transformer. Whichever method is used, it must be kept in mind that selectivity is not merely a matter of relay design. It also depends on the correct coordination of current transformers and relays with a suitable choice of relay settings, taking into account the possible range of such variables as fault currents, maximum load current, system impedances and other related factors, where appropriate. The term ‘stability’ is usually associated with unit protection schemes and refers to the ability of the protection system to remain unaffected by conditions external to the protected zone, for example through load current and external fault conditions.
Conventional earth fault protection using overcurrent elements fails to provide adequate protection for transformer windings. This is particularly the case for a star-connected winding with an impedance-earthed neutral.
The degree of protection is very much improved by the application of restricted earth fault protection. This is a unit protection scheme for one winding of the transformer. It can be of the high impedance type or of the biased low impedance type. For the high-impedance type, the residual current of three line current transformers is balanced against the output of a current transformer in the neutral conductor. In the biased low-impedance version, the three phase currents and the neutral current become the bias inputs to a differential element.
The system is operative for faults within the region between current transformers,  that is, for faults on the star winding in question. The system will remain stable for all faults outside this zone.



The gain in protection performance comes not only from using an instantaneous relay with a low setting, but also because the whole fault current is measured, not merely the transformed component in the HV primary winding (if the star winding is a secondary winding). Hence, although the prospective current level decreases as fault positions progressively nearer the neutral end of the winding are considered, the square law which controls the primary line current is not applicable, and with a low effective setting, a large percentage of the winding can be covered.
Restricted earth fault protection is often applied even when the neutral is solidly earthed. Since fault current then remains at a high value even to the last turn of the winding (Figure below), virtually complete cover for earth faults is obtained. This is an improvement compared with the performance of systems that do not measure the neutral conductor current. Earth fault protection applied to a delta-connected or unearthed star winding is inherently restricted, since no zero sequence components can be transmitted through the transformer to the other windings.
Both windings of a transformer can be protected separately with restricted earth fault protection, thereby providing high-speed protection against earth faults for the whole transformer with relatively simple equipment. A high impedance relay is used, giving fast operation and phase fault stability.



For ct characteristics determination you can follow according to below example:



Operation is required for a primary earth fault current of 25% rated earth fault current (i.e. 250A). The prime task in calculating settings is to calculate the value of the stabilizing resistor Rstab and stability factor K.
A stabilizing resistor is required to ensure through fault stability when one of the secondary CT’s saturates while the others do not. The requirements can be expressed as:




 
Author : Hamid - From: Iran
 