what is the recommended setting on the directional over current relay in ring / mesh network  & for coordination how can we set between two relays like 0.3 sec time discrimination.
Author : Ikhan - From: UK
 
#1
Sat, August 3rd, 2013 - 11:02
Refer to ALSTOM PROTECTIVE RELAY APPLICATION, section 9.15 for time grading of directional over current relay in ring mains.

The usual grading procedure for relays in a ring main circuit is to open the ring at the supply point and to grade the relays first clockwise and then anti-clockwise.
That is, the relays looking in a clockwise direction around the ring are arranged to operate in the sequence 1-2-3-4-5-6 and the relays looking in the anti-clockwise direction are arranged to operate in the sequence 1’-2’-3’-4’-5’-6’, as shown in Figure below.
The arrows associated with the relaying points indicate the direction of current flow that will cause the relay to operate. A double-headed arrow is used to indicate a non-directional relay, such as those at the supply point where the power can flow only in one direction. A single-headed arrow is used to indicate a directional relay, such as those at intermediate substations around the ring where the power can flow in either direction.
The directional relays are set in accordance with the invariable rule, applicable to all forms of directional protection, that the current in the system must flow from the substation busbars into the protected line in order that the relays may operate.
Disconnection of the faulted line is carried out according to time and fault current direction. As in any parallel system, the fault current has two parallel paths and divides itself in the inverse ratio of their impedances.
Thus, at each substation in the ring, one set of relays will be made inoperative because of the direction of current flow, and the other set operative. It will also be found that the operating times of the relays that are inoperative are faster than those of the operative relays, with the exception of the mid-point substation, where the operating times of relays 3 and 3’ happen to be the same.
The relays that are operative are graded downwards towards the fault and the last to be affected by the fault operates first. This applies to both paths to the fault.
Consequently, the faulted line is the only one to be disconnected from the ring and the power supply is maintained to all the substations.
When two or more power sources feed into a ring main, time graded overcurrent protection is difficult to apply and full discrimination may not be possible. With two sources of supply, two solutions are possible. The first is to open the ring at one of the supply points, whichever is more convenient, by means of a suitable high set instantaneous overcurrent relay. The ring is then graded as in the case of a single infeed. The second method is to treat the section of the ring between the two supply points as a continuous bus separate from the ring and to protect it with a unit protection system, and then proceed to grade the ring as in the case of a single infeed. Section 9.20.4 provides a worked example of ring main grading.


 
Author : Hamid - From: Iran
 