Electrical riddle No.37 - High current circuit breakers
Author : Mohammed - From: Syria
Thu, June 11th, 2009 - 18:22
1-For overcome of repulsion forces of circuit breaker contacts due to high through fault currents
2-For reduction of repulsion forces between moving electrical contacts of circuit breaker

As you know, fundamentally there is a current constriction at the point of electrical contact. We also know that this constriction is responsible for the contact resistance and consequently for the heat being generated at the contacts, but in addition to this the current constriction is also the source of electromagnetic forces acting upon the contact structures. In below Figure the current path of the current at the mating surface of the contact is shown.

As it can be seen from the figure, as the current constricts into a transfer point there is a component of the current that flows in opposite directions and thus the net result is a repelling force trying to force apart the contacts.
The repulsion force is given by:

F=10-7. I2 . ln (B/a)    Newton


B = Contact area
a = Actual area of contact point

With increasing of electrical contact pressures, the concentrated current area (a) can be increased which cause the reduction of repulsion forces.

It is difficult however to properly use this formula because of the difficulty in defining the actual contact area. For practical purposes some expressions that yield adequate results have been proposed.
For example:

F= 0.115 (I/n)2   lb.per finger

Or practical relationship which was obtained experimentally with a 3 inch Cu-Cr butt type contact in vacuum is given by the expression:

F= 0.885 (I/n)1.51   lb.per finger


I = Peak current in kA
n = Number of contacts

The differences on the force requirements obtained depending on which expression is used serve to point out the uncertainty of the variables involved and the probabilistic nature of the forces. In general the application of higher forces would yield a higher confidence level and a higher probability of withstanding the repulsion forces.