Switchgear Question No.1 - Switchgear ventilation
What requirements and criteria shall be considered in choosing of power switchboard ventilation system?
Author : Farzad - From: Iran
 
#1
Sat, July 4th, 2009 - 19:18
Switchboards and switchgear have a short-term maximum temperature of 40 °C and a maximum value of 35°C for the 24h average. BS 60439 states a maximum indoor ambient temperature of 40ºC, a maximum daily average of 35ºC and a minimum ambient of -5ºC.
As a general guidance rule, the temperature within the switchboard should not exceed 50/55ºC. If Switchroom/Plant room ambient is typically considered to be up to 25ºC this relates to a 25/30K rise above ambient. In the maximum ambient condition of 40ºC, this relates to a 10/15K rises above ambient. Natural ventilation facilities will be required in the design of the switchboard to ensure the maximum internal temperature is not exceeded.
The sources of heat within the switchboard will be:

a) Heat liberated by the copper work and cabling.
b) Heat liberated by the devices.
c) Heat liberated by eddy currents and magnetic losses.

A Factory Built Assembly accommodates a number of devices in a configuration that relates to the scheme requirements. The enclosure and compartments within it provide the operating environment for each device. Most devices e.g. circuit breakers, fuse switches; contactors etc. have been Type Tested in free air or “other enclosures”.
When enclosed within a switchboard compartment the heat liberated may adequately dissipate by convection and radiation from the “walls” of the enclosure and by heat sink via the conductors. It may however be necessary to assist the liberation to atmosphere by forced ventilation. Devices, which invariably require such measures, have by experience been found to be:

(a) ACB’s above 2,500A
(b) PFC Capacitor Banks
(c) Variable Speed Drives
(d) Motor Starting Resistors
(e) Power Transformers

In compliance with relevant DIN and VDI requirements, the following simplified installation configuration can be used:

– Ventilation devices and installations for ventilation and exhaust, e.g. when the permissible ambient temperature is higher than the (max.) outside temperature.





– Refrigeration units and installations for heat exhaust only, e.g. when the permissible ambient temperature is equal to or less than the (max.) outside temperature.



–Air-conditioning units and installations for air-conditioning, when in addition to heat removal specific ambient climate conditions are required (temperature, humidity, air quality, etc.).



Natural ventilation via louvers and/or mesh screens is the simplest and most cost effective measure of controlling temperature rise provided that I.P. ratings are agreed with the client. Considerable investigation has been carried out by AF Switchgear, to establish a relationship between watts dissipated and Inlet and Outlet louver free area required.
The problems arising from eddy currents and magnetic losses are generally overcome by common good practice in the selection of appropriate non-ferrous materials and the avoidance of ferrous metal “magnetic loops” being created in structures in close proximity to conductors or groups of conductors where phase/neutral balance may not prevail.
The subject of these sources of heat is often considered as one but is in fact two separate issues. Eddy Current heating results from the I²R losses of induced currents circulating in metalwork, which is not part of the defined conductor system. The use of non magnetic, low resistance materials such as Aluminum and Brass for single core cable gland plates and equipment mounting back plates (e.g. for circuit breakers above 630A) will reduce this source of heat and is advisable. Magnetic Heating results from the energy dissipated through each cycle of magnetization and de magnetization of a ferrous material (hysteresis loss) and relates to the metallurgical specification of the material used. Both these issues and the losses associated with them are frequency related and will be adversely affected at frequencies above the fundamental (50Hz).
Ferrous metal “magnetic loops” around single conductors or groups of conductors that do not produce a magnetic nil balance can bring about additional problems to those mentioned above by virtue of the fact that currents are circulating in metallic structures and joints in them that are not designed as conductor systems. These currents can be of extremely high magnitude, particularly during short-term load inrush transients and during short circuit conditions. Such high current circulations through joints in the structures can result in arcing / sparking at such joints. The arcing can produce an ionized gaseous state in a region close to the main conductors / busbars and precipitate a most catastrophic flashover and destructive failure in this zone of the switchboard. In situations where mechanical support is required between conductors, non-magnetic materials and sometimes non-metallic materials, have to be applied.
Forced ventilation via fan(s) will have to be considered if natural ventilation will not adequately maintain an acceptable environment for the device(s). Fans should be arranged to provide positive pressure (blowing in at low level) with exhaust air discharging at high level. It is generally advisable to use fans with integral louver/filter housings regardless of the I.P. requirements.
In situations where the I.P. rating of fan ventilated systems is not acceptably high enough or the temperature rise cannot be adequately controlled by this method – Refrigerated (A/C) cooling techniques must be employed.
Anti-condensation control may have to be incorporated either resulting from specified requirements or if the operating environment requires it. This may be catered for by thermostatically controlled heaters and/or ventilation. Special anti-condensation paint on internal surfaces is also effective in some cases.
 
Author : Hamid - From: Iran
 