Switchgear Riddle No.16 - 4 pole ELCB oprating working principle
what is a 4 pole ELCB oprating working principle?
as we know 2 pole elcb works on the comparison between phase and nutral current but what about the 4pole ELCB?
Author : ASAD ALI - From: Pakistan
Sat, November 12th, 2011 - 11:52
These devices operate on the principle of differential current measurement, in which any difference between the current entering a circuit and that leaving it, must (on a system supplied from an earthed source) be flowing to earth, either through faulty insulation or through contact of an earthed object, such as a person, with a live conductor.
Essential operation of 2 pole and 4 pole RCD is similar, the essential features are shown diagrammatically in figure below .

A magnetic core encompasses all the current carrying conductors of an electric circuit and the magnetic flux generated in the core will depend at every instant on the arithmetical sum of the currents; the currents passing in one direction being considered as positive, while those passing in the opposite direction will be negative.
In a normally healthy circuit i1 + i2 = 0 (i1+i2+i3+In=0 in 4 pole system) and there will be no flux in the magnetic core, and zero e.m.f. in its coil. An earth-fault current id will pass through the core to the fault, but will return to the source via the earth, or via protective conductors in a TN-earthed system. The current balance in the conductors passing through the magnetic core therefore no longer exists, and the difference gives rise to a magnetic flux in the core.
The difference current is known as the "residual" current and the principle is referred to as the "differential current" principle.
The resultant alternating flux in the core induces an e.m.f. in its coil, so that a current i3 flows in the tripping-device operating coil. If the residual current exceeds the value required to operate the tripping device, then the associated circuit breaker will trip.

Standard residual-current devices, referred to as RCDs, sufficiently sensitive for direct contact protection are rated at 30 mA of differential current. Other standard IEC ratings for high-sensitivity RCDs are 10 mA and 6 mA (generally used for individual appliance protection).
This additional protection is imposed in certain countries for circuits supplying socket outlets of ratings up to 32 A, and even higher if the location is wet and/or temporary (such as work-sites for example).

RCDs are commonly incorporated in the following components:

- industrial-type moulded-case differential circuit breakers conforming to IEC 947-2 and its appendix B,
- domestic-type differential circuit breakers (RCCBs)* conforming to IEC 755, 1008, and 1009 (RCBOs),
- differential switches conforming to particular national standards,
- relays with separate toroidal (ring-type) current transformers, conforming to IEC 755.

Author : Hamid - From: Iran- Firoozabad Fars
Sun, February 10th, 2013 - 07:14
Dear Mr. Hamid,

Good morning. I read your topics about RCD which is really helpful. But my question about the opearting principle of 4 pole RCD. Normaly the  RCD will work by the resultant current  i.e. vector sum of currents of all the three phases. But if the load is unbalanced then the vector sum of three phase currents will not be zero which cuase the  4 pole RCD to trip. Another thing if the 3rd harmonics present in the current, then 3 times phase current will flow to the neutral which cuase the RCD to trip. Please advise me how I wil install the 4 pole RCD if 3rd harmonics are present in load.


Tapas Barua.        
Author : Tapas Barua - From: Bangladesh
Mon, February 11th, 2013 - 08:46
Unbalanced load cause the residual currents that flow through neutral wire in 4 wire systems which do not have any effects on 4 pole RCD. In grounded 3 wire system, the residual current due to unbalanced load or/and harmonic currents should be considered in earth fault/leakage protection. 
Author : Hamid - From: Iran
Sun, June 23rd, 2013 - 11:05
sir i want to know that, how to install an ELCB in house wiring?
will you please guide me ? 
Author : Adnan Khalid - From: Pakistani
Sun, June 7th, 2015 - 16:37
thank you  
Author : Anil kumar - From: India
Mon, July 6th, 2015 - 20:50
Can we use 3Φ 4 pole elcb in 1Φ supply......? 
Author : Thilak - From: India
Tue, July 7th, 2015 - 08:43
Yes, please refer to following diagram.

Author : Hamid - From: Iran
Sun, August 23rd, 2015 - 16:07
Dear Sir,

Which RCCB/ ELCB use for three phase Arc welding m/c? 
Author : Vikas Pathare - From: India
Wed, September 16th, 2015 - 11:58
Dear Senior Experts,
i am shifting power supply from generator and utility supply to home by relays, my question is that can i use magnetic contacter in the place of relays? 
Author : Imran Javed - From: Pakistsan
Wed, September 16th, 2015 - 14:48
Please more explain, as you know auxiliary relay is used in control circuit and magnetic contactor is used in power circuit, how you can do that replacing? 
Author : Hamid - From: Iran
Sun, June 19th, 2016 - 12:59
Dear Sir,

How about phase to phase short circuit for 3 phase system, will the 3/4 pole RCCB will detect the fault? 
Author : Tan - From: Singapore
Wed, June 22nd, 2016 - 08:09
The RCCBs couldn't detect phase to phase short circuit, however phase to phase to earth could be triped by them. 
Author : M.S Jafarpour - From: Iran
Thu, July 28th, 2016 - 12:22
will 4 pole rcd tip if load is taken unbalance
Author : A M M ziyard - From: Srilanken
Wed, August 3rd, 2016 - 10:52
No, just the through fault current via earthing system can cause ELCB trip. 